- 論壇徽章:
- 0
|
其中一臺 post 報錯
sc> poweron
sc> co
SC Alert: Host System has Reset
nsole
Enter #. to return to ALOM.
0:0>
0:0>Sun Fire[TM] T2000 POST 4.25.12 2008/03/23 13:52
/export/delivery/delivery/4.25/4.25.12/post4.25.x/Niagara/ontario/integrated (root)
0:0>Copyright 2008 Sun Microsystems, Inc. All rights reserved
0:0>VBSC selecting POST MIN Testing.
0:0>POST enabling threads: ffff
0:0>VBSC setting verbosity level 2
0:0>Start Selftest.....
0:0>Master CPU Tests Basic....Done
0:0>Init MMU.....
0:0>L2 Tests....Done
0:0>Test Memory....Done
0:0>Decode of Sparc Error Status Reg bits 00000000.30002000
0:0> 1 AFSR_PRIV: Set to 1 if error happened while privileged or hyperprivileged.
0:0> 1 AFSR_LDAU: Set to 1 if the error was a L2/DRAM ECC uncorrectible error
0:0> Sparc AFAR = 00000000.001b00c0
0:0>CPU 0 trap trace.
0:0> tl tt tstate hpstate tpc
0:0> 00 0032 00000099.3f001603 00000000.00000004 ffffffff.f0131f24
0:0> 01 0181 00000100.3f001002 00000000.00000004 ffffffff.f012da14
0:0> 02 0181 00000100.3f001002 00000000.00000004 ffffffff.f012da14
0:0> 03 0181 00000100.3f001002 00000000.00000004 ffffffff.f012da14
SC Alert: Host System has Reset
SC Alert: Host system has shut down.
一直卡在這里就不動了
另一臺
sc> showlogs
Log entries since APR 08 16:52:19
----------------------------------
APR 08 16:52:19: 00040065: "SYS_FAN at FT0/FM0 is OK."
APR 08 16:52:20: 0004004f: "Indicator SYS/TOP_FAN_FAULT is now OFF"
APR 08 16:52:24: 0004004f: "Indicator SYS/SERVICE is now OFF"
APR 08 16:52:24: 0004004f: "Indicator FT0/FM0/SERVICE is now OFF"
APR 09 02:16:13: 00040066: "SYS_FAN at FT0/FM0 has FAILED."
APR 09 02:16:14: 0004004f: "Indicator SYS/SERVICE is now ON"
APR 09 02:16:14: 0004004f: "Indicator SYS/TOP_FAN_FAULT is now ON"
APR 09 02:16:14: 0004004f: "Indicator FT0/FM0/SERVICE is now ON"
APR 09 02:16:14: 00040065: "SYS_FAN at FT0/FM0 is OK."
APR 09 02:16:16: 0004004f: "Indicator SYS/TOP_FAN_FAULT is now OFF"
APR 09 02:16:18: 0004004f: "Indicator SYS/SERVICE is now OFF"
APR 09 02:16:18: 0004004f: "Indicator FT0/FM0/SERVICE is now OFF"
APR 13 17:12:31: 00040066: "SYS_FAN at FT0/FM2 has FAILED."
APR 13 17:12:32: 00040065: "SYS_FAN at FT0/FM2 is OK."
APR 13 17:12:32: 0004004f: "Indicator SYS/SERVICE is now ON"
APR 13 17:12:32: 0004004f: "Indicator FT0/FM2/SERVICE is now ON"
APR 13 17:12:36: 0004004f: "Indicator SYS/SERVICE is now OFF"
APR 13 17:12:36: 0004004f: "Indicator FT0/FM2/SERVICE is now OFF"
APR 17 14:14:29: 0004004f: "Indicator FT0/FM1/SERVICE is now ON"
APR 17 14:14:31: 0004004f: "Indicator FT0/FM1/SERVICE is now OFF"
這邊發(fā)現(xiàn)風(fēng)扇 自己會off 在系統(tǒng)里面看message 沒有問題 用戶說機(jī)子自己會關(guān)機(jī) 我懷疑是 風(fēng)扇off 造成溫度過高 但是為什么風(fēng)扇自己會off? |
|